I just got my generator interlock installed. I have an 8kw (running watts) generator. Currently I can run both of my ac units on this generator but it bogs the generator down.
I only plan to run one ac unit in emergency situations. These soft starts reduce the starting amperage of the AC unit from 70 amps to around 20 amps.
Has anyone installed or used one?
Sent from my SM-S918U using Tapatalk
I only plan to run one ac unit in emergency situations. These soft starts reduce the starting amperage of the AC unit from 70 amps to around 20 amps.
Has anyone installed or used one?
EasyStart™ 368 Soft Starter
The EasyStart™ soft start motor starter supports 115 & 230V A/C motors & employs a 4-part start ramp sequence that offers the lowest possible start-up current.
www.microair.net
Sent from my SM-S918U using Tapatalk